On Tue, 20 Feb 2007 22:47:05 +0000, Adrian Graham wrote:
On 20/2/07 21:48, "Tony Duell" <ard at
p850ug1.demon.co.uk> wrote:
> THat's an odd fault. It's repeatable, yes?
In other words you turn it on,
> it runs for 5 minutes, then trips the mains. You cna then power it down,
> power it up again and it'll run for another 5 minutes...
Yep. Every time. I haven't timed it exactly, but it
will run for minutes
then give up; last night I had enough time to start playing with DCL and
leave it for a bit while I dug a manual out. Then everything went black :)
I had a problem like that, where I had a rack that was drawing close to the limit on a 20
amp breaker,
when I added the last system to the stack the problem began, after a few minutes of
runtime the breaker
would heat up and pop, I swaped the breaker out with a different one of the same size and
it that held just
fine. The circuit I moved the week breaker to, normally only runs 7 or 8 amps and it never
failed with the
light load.
I had a second breaker problem. After an extended power failure, I found that the circuit
would not carry
both the normal startup load with the additional of 2 large UPS's at full charge rate
on near dead batteries
during startup. Just about the time everything booted and came back up, the breaker would
have heated
up and poped. I pulled the external battery packs off, and let them charge the internal
batteries first and
then added one external pack at a time, untill I could get a larger circuit run to the
rack.
While you are at it, you might want to take a clamp on amp meter and balance the load
between phases.
You may be pulling more power on one phase. If you pull the voltage down on one side or
phase with an
unballanced load, the current load will go up and breakers will be more likely to overheat
and pop.
I was in a 3 phase box just yesterday that was running 17a, 23a, and 37a on each of the 3
phases.
The electric company bills based on the max load on any single phase, by moving about 10a
of load from
phase 3 to phase 1, we dropped the billable load the electric company sees from 37a to
27a, close to a
third. That should look good on next months electric bill.
Just a thought, back under my rock ....
The other Bob