On Mon, 26 Apr 1999, Daniel T. Burrows wrote:
"Daniel T. Burrows"
<danburrows(a)mindspring.com> wrote:
> Close but not quite right. For single phase installations the power
company
supplies
2 hots and neutral. This is a center tapped secondary and the
neutral is earthed at the service entrance.
No, for split-phase, the power company does not "supply" a neutral from the
distribution system. The neutral is *only* tied to the center tap of the
secondary and to ground. It is not tied to anything on the primary side of
the transformer; that would be bad.
That is what I was trying to decsribe above.
The
primary of this transformer
is fed from only 1 high voltage phase.
I don't believe this; it doesn't match the descriptions I've read
elsewhere.
I've always seen it shown in diagrams with the
primary connected across two
phases of the three-phase. Otherwise you need a high-current return path
somewhere else.
Take a close look at rural areas and there is only 1 High voltage line
present.
It is fed to the HT input of all the pole transformers.
To even the loading of the phases, the
transformers for split-phase service
have their primaries distributed between the three possible combinations of
the three phases.
When there are 3 phases available that sometimes is the case. Look closely
at the pole transformers and in most cases when there are 2 or more
transformers mounted on 1 pole there is only 1 HT input to each transformer.
If it were between phases there would be 2 HT inputs.
Dan
Which, of course, is not to suggest that other pole routings may well
carry a different HT phase to achieve that balance.
- don