Examination yesterday showed:
* All connectors have 4 pins, and one wire is green
* Labels in most of the gear just says "see manual" but two pieces are clear=
ly
(and multiply) labeled "wired for 208V"
* Schematics show everything wired phase-to-phase, no neutral
* 110V "convenience outlets" are run from a step-down transformer between 2 p=
hases
So, it appears to be 208V delta.
I can run this from a wye-output transformer, though, right? Its plate says 2=
08V phase-to-phase.
Sure you can.
Provided the phase-to-phase voltage is correct (208V in this case), it
doesn't matter if the supply is delta or star (Wye) connected. Just don;t
connected anything to the neurral point on the transformer.
-tony