On Wednesday, October 27, 1999 9:38 AM, Mike Ford
[SMTP:mikeford@socal.rr.com] wrote:
>I live in a 29 story building. I have 2000 pounds
of racks with CPUs in
my
>"lab" (a room 20' X 20'). I am
going to move in another 2-3 thousand
pounds
>of minis as I am going through my storage and
moving them up here. I am
also
>picking up more minis from a plant in the US. I am
placing the mini
racks
>along the walls in the hope that there is more
support there. A real
serious
>question I have is... Can a room in a building
like this support 5000
pounds
>or more? If someone here has experience with this
please tell me if this
is
>okay.
Buildings are designed to withstand both "live" and "dead" loads. A
"live"
load is one where the load is not constant or is moving. IE: people, wind,
etc... A "dead" load is a load that is constant or does not move. IE: the
structure itself.
Although local building codes dictate what loads the building must support,
they are usually pretty consistent. I did a search and found the following
reference:
According to the 1991 standard building code:
Occupancy or Use Live Load (psf)
-------------------------------------------------------------------
Libraries:
Reading rooms 60
Stack rooms (books and shelving) 125
Corridors, above first floor 80
Residential: Multifamily houses;
Private apartments 40
Public rooms 100
Corridors 80
Dwellings:
Sleeping rooms 30
Attics with storage 30
Attics without storage 10
All other rooms 40
So, for a 20' X 20' room in your building the allowable load should be:
20 x 20 X 40(psf) = 16,000 lbs.
If one of your neighbors has a large book collection, they may be putting a
greater load on the building than you are... :-)
Steve Robertson - <steverob(a)hotoffice.com>