On Sat, 2003-02-22 at 22:18, Fred N. van Kempen wrote:
My real question:
These UPSes have 3 load segments each. On the Compaq, I currently
use *2*. Is this the reason for its screaming? Does the total
load come from the three segments?
Fred, I'm betting the Compaq UPS is rated for 800VA per load segment.
If this is true, then that means you are trying to supply 1650VA from
two segments, which are rated for a total of 1600VA. Try
moving some of
the load to the third segment and see what happens.
--