On 21 March 2011 03:33, Tony Duell <ard at p850ug1.demon.co.uk> wrote:
[3 phase connections and RCDs]
I made a similar comment a couple of months back, and
somebody claimed
that the RCDs (earyh leakage trips, ELCBs, GFIs, whatever you call them)
to their computer room were set to trip at 100A. I queried this at the
time, but was assured such things were not uncommon. I am still a little
worried.
Sorry. Should have replied to that thread but the thread went sideways.
I am guessing the 100A phase to ground breaker that was being claimed
and the RCD/ELCB/GFI 30mA breaker are two different safety systems
designed to detect and break current for two different purposes. The
transmission network (at least in Australia where I have experience
with the transmission infrastructure) have a requirement to break the
current on a phase to ground/earth fault. This is to protect primary
plant and system stability more than than people coming in contact
with the conductors. At 66kV and above on lines designed to handle
10's to 100's of MVA, people are generally considered as self clearing
faults.
I seem to recall what was quoted was likely to be more of the
distribution system, which, at the current specified would be to
protect the local distribution transformer against a phase to
ground/earth or a phase to phase fault. It may also be the case that
someone recalculated the numbers and realised that the circuit
breakers may not be rated to break the fault current. Note that the
current that the circuit breaker is required to break when a fault is
present can be significantly larger than normal operating current.
Without seeing the wiring diagram of the installation and the
associated calculations, really it is all guesswork. Although, I too
would be a little concerned if some equipment (as opposed to large
plant) was leaking close to 100A of current to earth. That sort of
fault current to a low impedance earth would result in something
getting hot!
The RCD/ELCB/GFI are designed to break the current before it has a
change to interrupt the heartbeat, if someone forms a circuit between
a suitable active conductor and earth. This is a much smaller current
designed to protect installations where people are much more likely to
come into contact with the current carrying conductors.
Note that for the pedantic. I have tried to use ground and earth as
appropriate. Where I am using ground/earth, it is where I would be
expecting a three wire transmission system with the center of the Y
winding connected to a large metal pole driven into the physical earth
near the transformer.
[chomp]
Simon
--
------------------------------------------------------------------------