Determine if there is a potential between the aerial lead and the TV or
cable box.
A story, perhaps helpful, perhaps not:
A couple of years ago, the lights in my house dimmed and brightened
noticably when the refrigerator would turn on or I would toast bread or
iron a shirt. I came to the conclusion that the neutral lead into my
house had excessive resistance. It was only a volt or two change when I
measured it, so I didn't think it was a problem.
Later, I was changing some cable TV wires and noticed that one was
actually warm to the touch. I went out to the telephone pole where the
wire came out the soil from my house and it was HOT. I fiddled with the
wire a bit and it melted and came apart, throwing sparks as it did.
The neutral conductor in the underground cable into my house failed at a
buried junction. For some time, my house neutral currents were carried
by the cable company's coax shield. It is interesting that none of the
other "ground" connections carried much current back to the transformer
on the pole. There were 5 paths to the pole: the neutral that failed, a
groundrod, the water main, the gas main, and the cable wire, and all the
current seems to have gone through the cable wire.
-chuck