A useful trick is to connect a 100W mains light
bulb in series with the
input to the transformer when first applying power (and with the
secondaries of the transformer unconnected). Such a bulb will easily
handle the magnetising current of a small transformer, anf won't even
glow (or drop much voltage), so you can check the output voltages, etc.
Hmmm, the way I'd do is to hook up one winding to the mains, then tie one
lead of the second winding to either side of the mains supply and measure
the voltage between the other lead and the other side of the mains supply.
If correctly phased, the voltage difference will be closer to 0 than
2xmains.
Sure. And you still use a series light bulb in case you get it wrong (or
your meter is malfunctioning, or...). In fact you can use the bulb for
the initial test, it'll drop almost no voltage so you'll get over 100V
(from your mains) across the primary. Easily enough to see if you get 0
or 200V between the free ends.
No, I'm not afraid of the mains, but I do treat it with respsect.
-tony