High-leg delta is independent of open- or
closed-delta.
That's correct.
Open delta uses two single-phase transformers
primaries connected to
phases AB and BC.
A to C is also valid, presumably it's rotated if there's a lot of open delta in an
area (again, why?) to balance phases.
On high-leg, one of the secondaries is center-tapped
and split
single-phase is fed from the center tap and either end of the secondary.
Right, and you get a mostly unusable "high leg" w.r.t. neutral, usually 208V
though I don't know what it ends up actually being in open delta with poor/uneven
loading. The 120/240 power available is also supposed to be derated, IIRC it's only
supposed to be 5-10% of total service load.
High-leg delta exists so you can have 120/240 lighting and appliance loads in a building
that consumes mostly 3-phase, like a machine shop with an office. In most areas you
aren't allowed to have more than one type of service to a building (not sure if
that's true for double-fed sites, never seen one with two kinds though). I've
heard the Power Company usually doesn't want to install high-leg delta anymore for a
variety of reasons: the load limit, people not understanding they need to skip a breaker,
120/208Y having become the usual form of smaller service three phase, etc.
Said configuration can be a 3-winding full delta
configuration or the
open-delta as detailed above.
Right, there's one or two of those services in town here for a couple of small
commercial buildings. Four wire high leg open delta off the pole, two transformers on the
pole.
Thanks,
Jonathan