Steve Robertson wrote:
You sure about that?
Yep. I asked my local NEC language lawyer about it before posting.
From what I understand, every conductor must be
capable of carrying a
current greater than the breaker that protects it. Otherwise, the cord
would
be the first thing thing to fail in a overcurrent
situation. This would
present a very significant fire danger.
In the context of building wiring, yes. Not in the context of appliance
wiring. 22GA zip cord, such as found on US lamps, isn't capable of
sustaining 20A@115V without heating -- and you can certainly plug a
15A plug into a 20A receptacle. In a catastrophic overcurrent situation,
i.e. a dead short, the breaker will long before the cord even warms. It's
the failure mode where the appliance draws more than it's designed to
draw but less that the branch protection rating that the problem occurs --
which is why most consumer electronic devices have mains protection sized
to their demand and most kitchen appliances have self-resetting thermal
overload cut-outs.
Even the cheapest kitchen appliances have fairly heavy
power cords. It's
not
because they draw a lot of current or the
manufacturers are generous, it's
because the fuses / breakers in your kitchen have a higher amperage rating
than in other places in the home. So, those appliances must have heavier
cords to offer protection.
Your home, maybe :-). Every branch in mine is rated at 20A. The reason
_most_
kitchen appliances have heavy cords is because _most_ of them are double
insulated. Then again, I've got an electric kettle that has a regular zip
cord on it -- and yes, it heats up during operation.
--