On 2011 Feb 5, at 7:27 AM, Tony Duell wrote:
The
real-world difference between North American 240V and Euro 240V
is=20=
the maximum potential relative to ground:
NA: 120 VRMS, 170V peak
Euro: 240 VRMS, 340V peak
That's one difference. The other difference is that in the States you
have a centre-tap available.
? The centre-tap is there as an outcome of the design, not innate
intent.
The peak voltage from the power-carryingwires to ground is also an
outcome of the design.
My real point is that no device that requires 220V should care about the
voltage to ground (within reason). I would certainly consider a 220V
device that could not satand 220V between one of the power-carrying wires
to ground ans being unsafe.
But as various people have pointed out, many US 220V appliances do use
110V for something (controller, timer, etc). That's a bigger problem when
running them in Europe
Actualyl, I have amn instrument (I think it's my Tektronix 575 curve
tracer) whic hahs sepprate wiring arrangements for 115V, 230V with the
centre earthed and 230V with one side earthed. No, the last 2 are not a
safety thing. Appranetly by having certain points of the transformer
primary close ot ground you get slightly less noise in the instrument.
-tony