It is a point-to-point RS-485 link, in this particular installation, not
multi-drop, fortunately.
I presume I would just tie the enable pins to "true"
The RS-485 device in question is a simple 4-wire transmit/receive pair.
I don't understand why you need a converter anyway. RS422 and RS485 use
the same voltage levels AFAIK. RS422 uses two pairs of wires: one for
sending and one for receiving. Devices are daisy-chained. RS485 uses one
pair of wires, for both sending and receiving. Some RS485 devices have
seperate terminals for the sending and receiving wires, so they are in
fact RS422 devices. Normally those wires are connected in parallel, so
that the devices also receives what it sends.
There is basically one situation that has to be avoided and that is two
transmitters connected at the same time. If you say that you RS485
device has 4 wires, I'd guess it has 2 for sending and 2 for receiving,
so it would simply connect easy to the RS422 device.
BTW, a common mistake is that people think that since RS422/RS485 are
differential busses, the ground does not have to be connected. I once
red a very good article on this topic that explains that the grounds of
all devices should _always_ be connected.
Correct me if I'm wrong.
--