Ian King (IanK at
vulcan.com) wrote:
We *are* running the machine off three separate 110V single-phase circuits
-
apparently you missed that part.
People need to understand the danger in this - in any multiphase power
system, the neutral current is the DIFFERENCE of the current in the
individual phases. If the load is perfectly balanced, then the neutral
current will be zero.
But, if you run the same load from three separate single phase circuits
and (worst case) the three circuits are all the same phase, then the neutral
current will be the SUM of all three phase currents. That's 3 times what it
would be otherwise and runs a serious danger of melting the neutral and
starting a fire.
Actually I thought the DEC power controllers had a circuit breaker in the
neutral leg too just to prevent somebody from doing something like this.
The split phase models do - are the three phase power controllers different
?
Bob