On 07/10/2011 12:52, Tobias Russell wrote:
I've just got hold of a pair of PDP-11/35s that
have 110V power supplies.
What is the collectives view on the best way of running these in the UK?
Is it safe to use a step down transformer (one of these for example:
http://www.ebay.co.uk/itm/3-3-KVA-SITE-TRANSFORMER-110-VOLT-110V-UK-SUPPLY-…)
or can I change the setup of the PSU to work from 220V?
It's safe, but not very efficient, and there a few other considerations.
First, you need to realise that a lot of those big yellow site
transformers are not rated for continuous use at the load they claim.
They're intended to run power tools which by their nature are used
intermittently. I don't know about that particular one, but most need
derated by 50%-75% for continuous operation.
Secondly, they produce 55-0-55VAC, ie centre-tapped to ground. Probably
not an issue, but you should be aware of it.
Lastly, although transformers can be very efficient, no transformer is
100% efficient (80%-90% is more typical).
The 11/35 (ditto the 11/40, like mine) uses an H742 supply to drive the
power bricks. It has a terminal strip inside that you can easily jumper
for either 110V or 230V, so there's no reason not to just change it.
Well, no reason except the damned thing is VERY heavy and therfoe
awkward to handle, but you already know that :-)
--